thorter wrote: 05 Jul 2025, 21:48
As someone with some experience but no expertise in control systems, the recent Spanish grid collapse looks suspiciously like running out of capacity. Think car alternator, and at some point of increasing load it will reach the limit that the excitation can provide for. The voltage then droops. The grid is much more complex with distributed generators, with the control effected using both the voltage and the frequency. If the specified narrow limits are not achieved, disconnections or tripping are the safeguards.
As a taster, and to tempt in the mildly interested.....

here's a snippet from the web article I linked to:
"On 28 April, at around 12:30 pm local time in Spain, just before the grid collapsed, renewable sources accounted for 78% of electricity generation on the Iberian system, with solar accounting for almost 60%. By contrast, conventional generation, such as gas and nuclear power plants, comprised only around 15% of the total generation mix.
According to Raúl Bajo Buenestado of the Baker Institute, two consecutive generation loss events occurred in southwestern Spain, likely involving large solar installations. “In just five seconds, Spain lost approximately 15 GW of capacity, equivalent to 60% of its national electricity demand. The remaining generation was insufficient to meet demand, thus triggering a cascading failure across the entire grid. Various generating units were automatically disconnected to protect infrastructure, and nuclear plants were shut down in accordance with safety protocols.”
Now, according to reporting by Reuters, the first official report by the Spanish authorities has blamed REE for miscalculating its power capacity needs on 28 April, meaning that a surge in voltage led to a massive blackout. REE did not have enough thermal power stations switched on during peak hours according to Spain’s Energy Minister Sara Aagesen in a news briefing in Madrid.
The report describes the blackout as being “caused by an overvoltage problem with a multifactorial origin: the system had insufficient voltage control capacity, there were oscillations that conditioned the operation of the system and disconnected generation facilities, in some cases in a seemingly undue way”.
And.....
"Phase1: Oscillations in the system (12:00 – 12:30)
At 12.03 pm an atypical oscillation of 0.6 Hz was recorded, which caused large voltage fluctuations for 4.42 minutes. This oscillation forced the System Operator to apply measures to cushion it, such as increasing the grid meshing – restricted by low demand – or reducing the flow of interconnection with France. All these actions dampened the oscillation, but had the side effect of increasing voltage. At 12.16 pm the same oscillation was recorded again, this time smaller, and 3 minutes later there was a further oscillation of 0.2 Hz. The System Operator applied the same measures to cushion it, which also contributed to increasing the voltage.
PHASE 2: Generation losses (12:32:57– 12:33:18)
Voltage began to rise rapidly and steadily, and numerous and progressive disconnections of generation facilities were recorded in Granada, Badajoz, Segovia, Huelva, Seville, Cáceres and other provinces.
PHASE 3: Collapse (12:33:18 – 12:33:30)
The progressive increase in voltage caused a chain reaction of overvoltage disconnections that could not be contained, as each disconnection contributed to further increases in voltages. There was also a drop in frequency that led to the loss of synchronisation with France. The interconnectors with France tripped, and the Iberian peninsular saw its power grid fall to zero."
......."But what is striking from this initial report into the Iberian blackout is that there is still no explanation for the initial cause. Three generators didn’t just trip off at the same time for no reason – the frequency oscillations described triggered their trips. But the report is silent on the origin of those oscillations. I suspect that if there had been some mundane grid fault, this would have been made public, which leads me to suspect we’re dealing with inverter-induced oscillations, something they would be reluctant to admit. We shall have to see if more comprehensive subsequent reports uncover more detail."
https://watt-logic.com/2025/06/18/shoul ... quirement/